Ok, lets say you need to provide secondary short circuit and internal fault protection for a 115kv - 34.5kv D-Y transformer on a radial transmission line supplying a rural distribution substation. Would it be better to to use step distance relaying with an over reaching zone through the transformer or over current elements instead? Anything special to consider when adding the positive sequence impedance of the transformer to the positive sequence impedance of the transmission line or is it way more complicated?
The transformer in question is 25/35/40 MVA with an R of 0.01363 and an X of 0.43186
{Yes I know people will ask why not send a DTT signal to the supply station when differential kicks in, but I'd like to have redundant protection if the PLC fails}