Xray supplier, Has requested the Z values are to be check at three separate points, What type of instrument/procedure should be followed. Job was designed and they informed us after the fact.
Have a 180 foot 4wire (4/0- # 4G) To Main 480 Volt Panel Fused at 200. Then to two different points for the xray unit..
There is no Transfromer. We are cannot To Bus Bar type assembly that travels up the Tower.
I will upload a photo if anyone requests.
Thank You
Have a 180 foot 4wire (4/0- # 4G) To Main 480 Volt Panel Fused at 200. Then to two different points for the xray unit..
There is no Transfromer. We are cannot To Bus Bar type assembly that travels up the Tower.