Re: impedence grounded
Don gave you the code, I would like to expand a little. A resistance or impedance grounded system is used where 3-phase, 3-wire critical load is much larger than single phase loads requiring a grounded conductor. Single phase loads will require an additional solidly grounded transformer.
This might have you asking why not just use a delta service. The answer would be a impedance or resistance grounded system shorts out the capacitance coupling to ground, and stablizes system voltages with respect to ground. This in turns reduces stress to cable insulation, other electrical components, and extends system life.