impedence grounded

Status
Not open for further replies.

plt

Member
what is impedence or resistance ground and how does it work? Is this mostly for motor loads or can lighting loads be placed on this system too?
where is this system covered in the code?
thank you.
 
Re: impedence grounded

See 250.36. This system cannot be used for line to neutral loads, it is only for line to line loads. A resistor or reactor is placed between the transformer XO and the grounding electrode system. This system can maintion power with a single ground fault as the impedance limits the ground fault current to a low value, often less than 10 amps. The system continues to work after a single ground fault, but if there is a second ground would occur on a different phase you will have a line to line fault.
Don
 
Re: impedence grounded

Don gave you the code, I would like to expand a little. A resistance or impedance grounded system is used where 3-phase, 3-wire critical load is much larger than single phase loads requiring a grounded conductor. Single phase loads will require an additional solidly grounded transformer.

This might have you asking why not just use a delta service. The answer would be a impedance or resistance grounded system shorts out the capacitance coupling to ground, and stablizes system voltages with respect to ground. This in turns reduces stress to cable insulation, other electrical components, and extends system life.
 
Re: impedence grounded

Bussmann's web site has some really nice power point slides on this type of thing. In This presentation it shows what happens (in diagram format) with a ground fault on all sorts of different systems. Its about a 2.5MB download, so if you have a dial-up it might take a few minutes. Worth the wait though, in my opinion.
 
Re: impedence grounded

Ryan,
This type of system is used mostly in industrial plants and places like utility generation plants, waste water treatment plants and similar occupancies.
Don
 
Re: impedence grounded

Originally posted by ryan_618:
Anything to considers its power to be crucial?
Yes. Anyplace where outages from L-G faults cannot be tolerated. Some more examples would be refinery, extrusion, induction furnace, pharmaceuticals, or any process where a interruption in service would cause re-tooling or excessive loss of production or product.
 
Re: impedence grounded

Another 2 cents worth is, it limits single phase to ground fault damage. It can either trip the component or allow an orderly shut down to find and repair a single phase to ground problem. The damage from a 5 or 10 amp fault at 10000 volts is much less than 100000 amps at 10000 volts.
 