Sparky_ron
Member
- Location
- Texas
- Occupation
- Master Electrician
So I have a dilemma and I’m looking for direction. Today I went to a customers business and they were having voltage issues. There is a fusable 400a 3-phase main disconnect, followed by a buss gutter. Im getting 208-210 a to b, b to c, and a to c, on the line and load side of the fuses however, I’m only getting 108 V on A, 135V on B, and 110 V on C.(phase to ground and phase to neutral.) With the fuses removed, I get 120 V on each phase on the incoming power side so I know it’s not a transformer issue. I also checked continuity on all three fuses because I didn’t have my fluke with me, (they are dual element fuses) and all appeared to be good. I have not opened up the gutter yet. I plan on going back tomorrow with my meter. What else could be causing the voltage to go so wonky with the fuses installed? Any help would be appreciated thank you.