G gerry Member Location New Jersey Jun 15, 2005 #1 Do I have to install a disconnect or switch at the filter pump location when the pump is hardwired with 240 GFI coming from interior sub-panel from garage about 40 feet away.
Do I have to install a disconnect or switch at the filter pump location when the pump is hardwired with 240 GFI coming from interior sub-panel from garage about 40 feet away.
charlie Senior Member Location Indianapolis Jun 16, 2005 #2 Re: in ground pool pump 680.12 requires a disconnecting means within sight but you do not need a GFCI since the pump is hard wired.
Re: in ground pool pump 680.12 requires a disconnecting means within sight but you do not need a GFCI since the pump is hard wired.