We have two in-ground pull boxes. Both are Christy N36 concrete electrical boxes (17" x 30" nominal internal dimensions). Each appears to have problems with the way the wire was pulled through the box. I'd like to get feedback on the seriousness of the problems, how they could have been avoided during construction, and how we can resolve the problems now.
Pull Box #1:
This box contains a single run of (3) 500 MCM CU-XHHW feeders carrying 3-phase 480VAC (no neutral) in 4" PVC conduit. In this box, the way the wires are looped means that the box lid is in contact with the tops of the wires. The box lid is composite (plastic top surface & cast concrete bottom surface) so the rough concrete bottom-side of the lid is rubbing against the insulation of the wires. There is some light scuffing/abrasion of the insulation where the wires contact the lid.
Pull Box #2:
This box contains two runs of (3) 500 MCM CU-XHHW feeders carrying 3-phase 480VAC (plus some additional runs of wire carrying DC from a set of solar panels); each run of feeders is in 4" PVC conduit. One set of feeders (center-top in photo) is very tightly looped to a very small radius. I'm concerned that this may reduce the longevity of the insulation. The other set of feeders is rubbing against three sides of the concrete box (top, right, and bottom sides in the photo). Also, the sand fill in the bottom of the box is up to the level of the opening of at least one conduit.
Additionally, this set of feeders is spliced but the shrink-wrap splice covers do not appear to be waterproof (no hot-melt adhesive is visible).
Pull Box #1:
This box contains a single run of (3) 500 MCM CU-XHHW feeders carrying 3-phase 480VAC (no neutral) in 4" PVC conduit. In this box, the way the wires are looped means that the box lid is in contact with the tops of the wires. The box lid is composite (plastic top surface & cast concrete bottom surface) so the rough concrete bottom-side of the lid is rubbing against the insulation of the wires. There is some light scuffing/abrasion of the insulation where the wires contact the lid.
Pull Box #2:
This box contains two runs of (3) 500 MCM CU-XHHW feeders carrying 3-phase 480VAC (plus some additional runs of wire carrying DC from a set of solar panels); each run of feeders is in 4" PVC conduit. One set of feeders (center-top in photo) is very tightly looped to a very small radius. I'm concerned that this may reduce the longevity of the insulation. The other set of feeders is rubbing against three sides of the concrete box (top, right, and bottom sides in the photo). Also, the sand fill in the bottom of the box is up to the level of the opening of at least one conduit.
Additionally, this set of feeders is spliced but the shrink-wrap splice covers do not appear to be waterproof (no hot-melt adhesive is visible).