I work for a Aquaculture research facility where they designed a recirculation system for salt water, and they want to heat the water. So they purchased a 3 phase, 240 volt, 18 KW (50 amp) in-line water heater. Does this unit require GFCI protection, and if so, what would be the milliamp trip for the unit be?
Do you want a code answer or a design answer?
Per code, since this is not a swimming pool or a hot tub, no GFCI would be required. There may be an obscure section related to industrial aquaculture that does say something though. I assume that this will not be cord and plug connected?
Per design, if workers are going to reach into the water frequently and maybe suit up and get in for maintenance, cleaning, or whatever, occasionally, I would feel better using some sort of GF detection. But I do not know what is available in three phase 50A breakers.
I do not think that the personnel protection 6ma threshold is necessary, or that the large heater would even meet that standard. On the other hand capacitive leakage from a three phase heating element could well average out close to zero ma.
The next threshold up would be ~30ma, which gives good life safety protection for casual contact, but might not be low enough for full body immersion where it would be difficult to get out once shocked.
I would certainly want to make sure that metal parts of the plumbing nearest the water heater are bonded, even if I did not have a full equipotential grid around the whole installation.
Salt water does make the whole thing more interesting, IMHO.