I have a client that wants an in-line terminal in a condulet type fitting downstream of the seal for ease of future device replacement. I have yet to find either a small terminal block (6 feed through spaces) or an inline method of providing the desired break for each conductor. The method needs to be rated for a class 1 division 2 area, and fairly small. Any help would be appreciated.
 
Not entirely sure what the nec says on it, I'm fairly new to the realm of 501, but at the least the client is requesting class 1 div 2 listed or listed as non-incendive. The design is trying to avoid the explosion proof enclosures.
 
It sounds like your client may have an IEC background or is influenced by someone who has one. Under "classic" IEC Zone concepts, terminals are considered "arc-making" and are required to be certified "EX e." Essentially, this means the terminal is "self-locking," "pullout resistent" and "vibration proof."

NEC does not require any of those features in Class I, Division 2 and enclosures for terminals only are not required to be explosionproof.
 
I should add you won't find a terminal marked for Class I, Division 1 either.

Your best bet is to get one marked "AEx e" which will have the IEC features I mentioned and is suitable for Division 2. See Section 501.5. Some of the "miniature" blocks may suit you, but be careful of the volume.
 
Hazardous location or not, the conduit body would still need enough volume to meet requirements of 314.16(C).
 
Yeah I'm leaning more and more towards politely telling the client that isn't going to be designed that way.
In that case, I have another suggestion. It is my opinion that properly installed "twist type" connectors, specifically with spring steel wire with a square (not round) cross-section (3M), probably meets most of the "AEx e" necessary requirements. They aren't (and will never be) listed for it though because the IEC standard 60079-7 wants terminal blocks and CENELEC (EU IEC Reps) wants the trade barrier. They are however suitable for US domestic Division 2, but not specifically listed. I specify them routinely, although they aren’t an absolute NEC requirement either. I also specify “AEx E” terminal blocks in Division 2, when I believe it’s appropriate
 
Last edited:
Bob, I don't want to hijack the thread, but this begs the question: when would you find it 'appropriate'?
Usually high-amplitude, low frequency vibration locations; typically large, low speed reciprocal compressors. It is belt & suspenders, but it?s usually a relatively low cost and I sleep a bit better.
 
I have a client that wants an in-line terminal in a condulet type fitting downstream of the seal for ease of future device replacement. I have yet to find either a small terminal block (6 feed through spaces) or an inline method of providing the desired break for each conductor. The method needs to be rated for a class 1 division 2 area, and fairly small. Any help would be appreciated.
In the past year I've work at a couple nuclear power plants. I've not been involved with part specifications or NQA-1. I can tell you in my limited experience what was used for a couple applications like you describe, but in areas that likely would not be NEC classified hazardous.

One method used was knife disconnect splice terminals. Here's a link to PIDG example http://www.te.com/catalog/pn/en/8-35762-2

The blade area of the splice was backwrapped with electrical tape, then raychem'd (thick-wall heat shrink with sealant adhesive on the inside) to a specified minimum distance beyond the terminals in both directions.

Another method was male-female connectors the name of which I cannot recall at present. The insulating mating boots were pliable like silicon-rubber. If I recall the name I'll post again.
 