T tonyjz Member Location Saint Joseph, Mo. Jun 28, 2013 #1 Have a solar installer that states the line and load can be in the same conduit. I disagree. Any thoughts?
Have a solar installer that states the line and load can be in the same conduit. I disagree. Any thoughts?
Ponchik Senior Member Location CA Occupation Electronologist Jun 28, 2013 #2 It depends what you mean by "LINE". If by "LINE" you mean "service" then you are correct. The service conduit can not have any other conductors in it. If as "LINE" you mean "feeder" then it is ok to have other conductors in the same conduit. (besides service conductors of course)
It depends what you mean by "LINE". If by "LINE" you mean "service" then you are correct. The service conduit can not have any other conductors in it. If as "LINE" you mean "feeder" then it is ok to have other conductors in the same conduit. (besides service conductors of course)
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jun 28, 2013 #3 Look at 690.4(B).