Russs57
Senior Member
- Location
- Miami, Florida, USA
- Occupation
- Maintenance Engineer
I had a couple of unusual experiences recently with VFD's. Thought I would share what I learned.
The first was a 125 HP chill water pump. Original drive was an older Altivar with drive output and bypass contactors and HOA switch. Drive was recently replaced with a newer Altivar but all the contactors/switches were kept. Every time the drive was reset, and it would ramp up past 10 hertz, the contactor would drop out. Drive fault was output phase fault. But the drive would self restart several times in a row, sometimes the output contactor would "chatter".
In the end it turned out some plastic pieces that secure the coil in place in the LC1F185 contactor had deteriorated over time. I am having no luck finding them as they actually attach to the laminated armature/pole. Looks like I have to fork out the bucks for a new contactor. All over a four plastic clips, one of which has a yellow pushbutton on it which is depressed to slide the coil out. This took some time to locate.
The second was on some new AHU's that happen to have two fan motors and two VFD's. Seems when one drive trips out but the other is still running, the motor on the off-line drive spins backwards and dumps back into the drive. You will notice faults like high DC bus voltage, over current, and/or short circuit faults. You will get these faults before the drive even takes off. Just shut down all drives, reset as needed, and fire them all up at the same time and you will be fine This might be self evident to many here but I wasn't used to such setups in AHU's and wasted some time with a megger and amp probe
The first was a 125 HP chill water pump. Original drive was an older Altivar with drive output and bypass contactors and HOA switch. Drive was recently replaced with a newer Altivar but all the contactors/switches were kept. Every time the drive was reset, and it would ramp up past 10 hertz, the contactor would drop out. Drive fault was output phase fault. But the drive would self restart several times in a row, sometimes the output contactor would "chatter".
In the end it turned out some plastic pieces that secure the coil in place in the LC1F185 contactor had deteriorated over time. I am having no luck finding them as they actually attach to the laminated armature/pole. Looks like I have to fork out the bucks for a new contactor. All over a four plastic clips, one of which has a yellow pushbutton on it which is depressed to slide the coil out. This took some time to locate.
The second was on some new AHU's that happen to have two fan motors and two VFD's. Seems when one drive trips out but the other is still running, the motor on the off-line drive spins backwards and dumps back into the drive. You will notice faults like high DC bus voltage, over current, and/or short circuit faults. You will get these faults before the drive even takes off. Just shut down all drives, reset as needed, and fire them all up at the same time and you will be fine This might be self evident to many here but I wasn't used to such setups in AHU's and wasted some time with a megger and amp probe