Do you guys have examples of less than effective 2008NEC continuing ed presentations of a code change ?
I have 4 off the top of my head from Article210. . I'll post more if/when I think of them.
1
210.4(D) + 210.4(D)X, OK so the continuing ed/changes instructor read the requirement but it would have been very helpful to the electrical contractor foreman or the electrical inspector to cover how to “pick up” on this.
Look into the panel and take note only of any homerun that have more than one neutral. . Do those homeruns have more hot conductors than neutrals ? . If yes, than look for application/compliance with 210.4(D) + X.
2
210.12(B), the instructor read thru the room list and just kept going. . I'm thinking in my mind, "Hold on a second ! . If you have a long list of what rooms are required to have AFCIs, then how about a short list of what's not required." . Such as:
the 3 categories of restricted load 20 amp circuits of 210.11(C)
1) 210.11(C)(1) small appliance in kitchen AND all other kitchen circuits [lighting, refridge etc] not AFCI required but the dining IS AFCI required
2) 210.11(C)(2) laundry not AFCI required
3) 210.11(C)(3) bathroom not AFCI required
and 3 of the 5 categories of areas not required to have plugs every 6 feet [areas not listed in 210.52(A)]. . Closets and hallways ARE AFCI required. . The 3 that are not required are:
1) 210.52(E) outdoor not AFCI required
2) 210.52(G) basements, unfinished section not AFCI required
3) 210.52(G) garage not AFCI required
3
210.12(B)X1 has the word “steel” in it. . Shouldn’t the continuing ed presenter mention that aluminum jacketed cable does not satisfy that exception ?
With MC AP taking off like a rocket, I’ll bet $1000 that we’ll see many residential/commercial electrical contractors pull AFCI plugs, metal boxes, and MC AP out of their truck for residential. . Am I wrong in concluding that all MC AP is aluminum jacket ? . I think this is going to be an issue on house roughs.
4
210.63 has a 25 foot limit. . The new section of 210.52(E)(3) has a “within the perimeter” spec. . A lot of spec houses with 2 outside plugs will now need 3 [depending on where the 25’ measurement falls].
David
I have 4 off the top of my head from Article210. . I'll post more if/when I think of them.
1
210.4(D) + 210.4(D)X, OK so the continuing ed/changes instructor read the requirement but it would have been very helpful to the electrical contractor foreman or the electrical inspector to cover how to “pick up” on this.
Look into the panel and take note only of any homerun
2
210.12(B), the instructor read thru the room list and just kept going. . I'm thinking in my mind, "Hold on a second ! . If you have a long list of what rooms are required to have AFCIs, then how about a short list of what's not required." . Such as:
the 3 categories of restricted load 20 amp circuits of 210.11(C)
1) 210.11(C)(1) small appliance in kitchen AND all other kitchen circuits [lighting, refridge etc] not AFCI required but the dining IS AFCI required
2) 210.11(C)(2) laundry not AFCI required
3) 210.11(C)(3) bathroom not AFCI required
and 3 of the 5 categories of areas not required to have plugs every 6 feet [areas not listed in 210.52(A)]. . Closets and hallways ARE AFCI required. . The 3 that are not required are:
1) 210.52(E) outdoor not AFCI required
2) 210.52(G) basements, unfinished section not AFCI required
3) 210.52(G) garage not AFCI required
3
210.12(B)X1 has the word “steel” in it. . Shouldn’t the continuing ed presenter mention that aluminum jacketed cable does not satisfy that exception ?
With MC AP taking off like a rocket, I’ll bet $1000 that we’ll see many residential/commercial electrical contractors pull AFCI plugs, metal boxes, and MC AP out of their truck for residential. . Am I wrong in concluding that all MC AP is aluminum jacket ? . I think this is going to be an issue on house roughs.
4
210.63 has a 25 foot limit. . The new section of 210.52(E)(3) has a “within the perimeter” spec. . A lot of spec houses with 2 outside plugs will now need 3 [depending on where the 25’ measurement falls].
David