arcsnsparks98
Senior Member
- Location
- Jackson, TN USA
This past week I was doing some work in an industrial facility where I noticed something I have never came across before. Mounted on the sides of a few of the machines were convenience receptacles. After paying closer attention I discovered they were fed from the 480/120 control transformer inside the control cabinet. I didn't see the exact VA rating but apparently it was enough that it could support a few amps at a receptacle. What concerns me is the fault current path return path in the event of a fault. Control transformers aren't intended to be utilized outside of the control cabinet and associated control wiring of the machine in which they are installed. The 120v secondary is floating in this case because one side of it is not bonded to ground.Am I correct in saying that in the event of a ground fault somewhere on this convenience receptacle circuit, there is not an effective return path to the source to allow for adequate protection? There are primary side fuses for the transformer but without fault current being able to return to it, I don't know that they would do much good. The ground from the receptacle is electrically connected to the ground from the primary so fault current could flow back to the building GES but that may not be sufficient to make it safe. Any thoughts?