Hi,
I am reviewing the arc flash study done for our plant and notice that the energy level at the main switchboard (GE Spectra with 4000A main) is in the 300+cal/cm2. The basic setup is 2500KVA, 12.47KV/480VAC, 5.82%Z to 25ft of 12- 400MCM per phase in buried duct to GE Spectra switchboard. The fuse on the primary side of the transformer is 150E, SMU-20 (slow). The engineer used the IEEE1584 equipment type and associated working distance and bus gap for the analysis. The notes said "assume PD not isolated". At any rate, if the energy is correct, we can not even do IR study in this space. Have anyone seen typicall IE for this type of setup? Seems crazy high to me. Something is amiss.
The other question is if a tech is to enter the electrical room and reset a breaker, does he not need to wear AR suit? There are no suit for energy that high. Any inputs would be greatly appreciated.
Regards,
FK
I am reviewing the arc flash study done for our plant and notice that the energy level at the main switchboard (GE Spectra with 4000A main) is in the 300+cal/cm2. The basic setup is 2500KVA, 12.47KV/480VAC, 5.82%Z to 25ft of 12- 400MCM per phase in buried duct to GE Spectra switchboard. The fuse on the primary side of the transformer is 150E, SMU-20 (slow). The engineer used the IEEE1584 equipment type and associated working distance and bus gap for the analysis. The notes said "assume PD not isolated". At any rate, if the energy is correct, we can not even do IR study in this space. Have anyone seen typicall IE for this type of setup? Seems crazy high to me. Something is amiss.
The other question is if a tech is to enter the electrical room and reset a breaker, does he not need to wear AR suit? There are no suit for energy that high. Any inputs would be greatly appreciated.
Regards,
FK