The existing building has 3 tenants with a electrical service off 400AMP/208V/3 Phase.
Based on the landlord work letter, the tenants are asking for the following service
Tenant A: 400AMP/208V/3 Phase [General Store]
Tenant B: 400AMP/208V/3 Phase [Fast Food]
Tenant C: 200AMP/208V/3 Phase [Fast Food]
2 Tenants will be fast food and the other one is a general store. There will be gas at this location and not be fully electric.
Can I use Table 220.88 and keep the existing 400 AMP service for the General store?
=(400+200)*360 = 216kVA
.5(216) + 200 = 308kVA [Table 220.88]
308kVA/360 = 856 AMP
Should I ask the utility company to update the service to 1200AMP/208V/3 Phase
What is the best method to calculate the new service.
Based on the landlord work letter, the tenants are asking for the following service
Tenant A: 400AMP/208V/3 Phase [General Store]
Tenant B: 400AMP/208V/3 Phase [Fast Food]
Tenant C: 200AMP/208V/3 Phase [Fast Food]
2 Tenants will be fast food and the other one is a general store. There will be gas at this location and not be fully electric.
Can I use Table 220.88 and keep the existing 400 AMP service for the General store?
=(400+200)*360 = 216kVA
.5(216) + 200 = 308kVA [Table 220.88]
308kVA/360 = 856 AMP
Should I ask the utility company to update the service to 1200AMP/208V/3 Phase
What is the best method to calculate the new service.