We have a 3 phase, 4 wire generator with an Earth Fault Relay supplied via a CT on the star point / neutral. Recently, the plant tripped due to activation of the EFR. Let it be noted there is some imbalance across the phases.
The CT fitted has worked with no issues for many years. It is 1600/5A. Upon restart and synchronisation of the generator the current in the secondary circuit was around 11-12A yet the current in the neutral was around 120A. Once the current in the generator calmed down, the current in the neutral was measured with a clamp meter as 45A (primary), with the Secondary CT circuit measuring 4.3A. The plants KWH meter also calculated close to 45A in the neutral.
With the CT being 1600/5A, it means that at 4.3A the primary would be 1376A (which it's not). For the 45A in the primary I would expect to see around 0.15A in the secondary.
The CT was replaced yet the problem persists. The next step is to investigate the CT leads to the relay and the relay itself. My question is what could cause the CT secondary to be so far out of proportion to the primary?
Thanks
The CT fitted has worked with no issues for many years. It is 1600/5A. Upon restart and synchronisation of the generator the current in the secondary circuit was around 11-12A yet the current in the neutral was around 120A. Once the current in the generator calmed down, the current in the neutral was measured with a clamp meter as 45A (primary), with the Secondary CT circuit measuring 4.3A. The plants KWH meter also calculated close to 45A in the neutral.
With the CT being 1600/5A, it means that at 4.3A the primary would be 1376A (which it's not). For the 45A in the primary I would expect to see around 0.15A in the secondary.
The CT was replaced yet the problem persists. The next step is to investigate the CT leads to the relay and the relay itself. My question is what could cause the CT secondary to be so far out of proportion to the primary?