Spotted today, fortunately the commenters are calling it out:
Why I think its wrong:
This is why I believe the terms "grounding" and "bonding" should be discarded altogether (misconception based origin) and replaced with Fault Loop Conduction and Automatic Disconnection of Supply.
Why I think its wrong:
- The ground (planet earth) is not capable of opening a breaker or fuse on a 120 or 230 volt circuit. The resistance of earth is to high.
- A main bonding jumper to the service neutral or system neutral allows high current to flow to promptly open a fuse or circuit breaker during a fault. Not earth.
- Electricity returns to the source, not the earth.
- Electricity takes all paths of resistance.
- touch voltage is still present on the metal frame of an appliance during fault even with a ground wire. Only the breaker opening or fuse blowing results in the voltage dropping to zero.
This is why I believe the terms "grounding" and "bonding" should be discarded altogether (misconception based origin) and replaced with Fault Loop Conduction and Automatic Disconnection of Supply.