Incorrectly added neutral ?

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I have a situation where a 4th wire (neutral) was added to a disconnect ( 3hots and ground input 3hots and ground and neutral output ground and neutral hooked to case) and i believe improperly??? Input appreciated????. There are currently no line to neutral loads but i think this could be a future problem. Also in this hand made diagram there are other overcurrent protection problems but I would like to concentrate on the neutral for now.

Thankyou you guys are a great help to my education

Dave
Neutral photo question.jpg
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I agree. It's at best a redundant EGC.

To be a neutral, it would have to have a direct connection to a secondary neutral.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I agree. It's at best a redundant EGC.

To be a neutral, it would have to have a direct connection to a secondary neutral.
Thank you for taking time to look at my crappy diagram. Btw that 400amp disco is fed by a cable 3 hits bare stranded ground
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You are correct. The neutral conductor should be eliminated or made a redundant EGC
Might be worth varifying that the gear is properly rated and not just rated for a 480/27 system.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
You are correct. The neutral conductor should be eliminated or made a redundant EGC
Might be worth varifying that the gear is properly rated and not just rated for a 480/27 system.
Thank you for your expertise and experience
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I agree. It's at best a redundant EGC.

To be a neutral, it would have to have a direct connection to a secondary neutral.
Thank you for your time this started as a tech in training installing an outlet for a monitor, he had some questions and the more I looked the worse things were. I omitted. several bad things with this install to concentrate on the neutral.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
You are correct. The neutral conductor should be eliminated or made a redundant EGC
Might be worth varifying that the gear is properly rated and not just rated for a 480/27 system.
I am going to be buying a new 480 panel cause the current one has no main and shares the tapped feed with a transformer. 125amp main lug panel fed from 400amp breaker not desired.
Since there is currently no neutral loads is there a special Panel i buy or just do not hook up neutral?


Working in that gear and pulling a new wire or cable is possible if the plant shuts down which we do not want to do. I would like the idea of having the neutral available but at this time its not necessary. There appears to be a few safety issues that need to be resolved.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If it is a 480 ungrounded or corner grounded system you need to make sure the panel is rated for that system.
There are panels on the market designed for 480/277 systems that, even thought they have a "480 rating", they are not suitable for 480 ungrounded or corner grounded systems
(Se 240.85 for additional information)
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Be sure to relabel that 480 volt panel once the netutal wire has been removed or changed. Surprised there is no main in the 120/240 panel after the transformer and no OCD in 480 volt only panel after tap.
Got your work cut out for ya.

I see the main switch gear is 480 three phase ?? Three or four wire .
grounded or ungrounded.
What type of system? You may other issues.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
If it is a 480 ungrounded or corner grounded system you need to make sure the panel is rated for that system.
There are panels on the market designed for 480/277 systems that, even thought they have a "480 rating", they are not suitable for 480 ungrounded or corner grounded systems
(Se 240.85 for additional information)
You must have posted why I typed.
He said plant I would be it's a 480 volt corner grounded delta. Just a quess
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Be sure to relabel that 480 volt panel once the netutal wire has been removed or changed. Surprised there is no main in the 120/240 panel after the transformer and no OCD in 480 volt only panel after tap.
Got your work cut out for ya.

I see the main switch gear is 480 three phase ?? Three or four wire .
grounded or ungrounded.
What type of system? You may other issues.
It is a 480volt wye I cant open the busway or gear to verify 3 or 4 wire (Arc flash policies) but I suspect 4. I have been digging around I think i have a Picture with the utility transformer open.

This single outlet job is the gift that keeps on giving. The 400 amp feed is 4/0 230amp plus 60ft away its tapped to a number #10 for a transformer. It goes on and on. I think at one point this portion of mill was knocked down due to a wind storm.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
If it is a 480 ungrounded or corner grounded system you need to make sure the panel is rated for that system.
There are panels on the market designed for 480/277 systems that, even thought they have a "480 rating", they are not suitable for 480 ungrounded or corner grounded systems
(Se 240.85 for additional information)
Thank you for your in put this one definitely is a wye
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IF it's a wye you can disregard my concern about the panel rating.
Since you have no neutral going to the fused disconnect that supplies your panel, there is no neutral path available at your panel.
 