Long story short on how I discovered this situation: outside scale technician found 132 VAC at a receptacle in our plant while troubleshooting a scale indicator.
I have a 125KVA 480/208 3ph transformer feeding three 200 amp panelboards. When the scale tech approached me about this, I immediately thought loose neutral somewhere so I started looking into it. After checking voltages and lug tightness at the panels and then at the disconnects and finding nothing, I moved on to the transformer. I found that the primary is wired to the 432 volt taps, creating secondary voltages of 133 L-N and 231 L-L.
The transformer is only about 100' from the service entrance (I didn't check conductor size) and the primary voltage was 479 normally loaded so it doesn't seem like voltage drop is an issue.
The contractor that did this install in the late '80's no longer exists and the company electrician at the time has passed away. The maintenance manager from that time says he's sure it was a permitted and inspected installation but I can't imagine this would have flown with an inspector.
Thinking about this again just now, is it possible that they did this to boost the L-L voltage up closer to 240 and the L-N voltage was acceptable to the installer? We do have several welder receptacles. Should I just reconnect to the proper taps? If not, what steps should I take first? I'm not so concerned with the "why" as I am with the "what should I do about it".
PS These panels feed nothing but receptacles and lighting. No three-phase loads.
I have a 125KVA 480/208 3ph transformer feeding three 200 amp panelboards. When the scale tech approached me about this, I immediately thought loose neutral somewhere so I started looking into it. After checking voltages and lug tightness at the panels and then at the disconnects and finding nothing, I moved on to the transformer. I found that the primary is wired to the 432 volt taps, creating secondary voltages of 133 L-N and 231 L-L.
The transformer is only about 100' from the service entrance (I didn't check conductor size) and the primary voltage was 479 normally loaded so it doesn't seem like voltage drop is an issue.
The contractor that did this install in the late '80's no longer exists and the company electrician at the time has passed away. The maintenance manager from that time says he's sure it was a permitted and inspected installation but I can't imagine this would have flown with an inspector.
Thinking about this again just now, is it possible that they did this to boost the L-L voltage up closer to 240 and the L-N voltage was acceptable to the installer? We do have several welder receptacles. Should I just reconnect to the proper taps? If not, what steps should I take first? I'm not so concerned with the "why" as I am with the "what should I do about it".
PS These panels feed nothing but receptacles and lighting. No three-phase loads.