I have branch circuit fed from 150A breaker to chiller rooftop. The circuit conductors go on roof so their is rooftop correction and temperature correction factor. The size of phase and neutral conductors are increased from 1/0AWG to 2/0 AWG.
My feelings say equipment grounding conductor which is wire should be increased however reading the handbook blue comments NEC 2014 Section 250.122(B) says in some cases, use of conductors with higher insulation temperature rating allows for compliance with
ampacity adjustment and correction requirements without having to increase the circular mil area of the conductor.
So I am confused should the EGC be increased in scenario first paragraph per NEC 2014 section 250.122(B) or it can be compliance without increase EGC size per NEC 2024 section 250.122(B)?