Hey all, I'm using 2011 NEC and copper conductors.
In theory, let's say we have 208Y120V serving a 35-40A generic load at 300' away (subpanel).
Solution A
50/3 breaker. Initial feeder size would be 4#8, #10G, 3/4"C but due to voltage drop, we'd want to increase the size of wire to say 4#3, #4G, 1-1/4"C (#4G using 250.122(B) rule for circular mil upsizing from the initial).
Solution B
100/3 breaker, keeping the wiring at 4#3, #8G, 1-1/4"C (EGC would be smaller and cheaper than above).
Which solution is best, and am I thinking about this wrong?? The #4G doesn't really make sense considering solution B. I would appreciate any thoughts about this, thanks.