jkassebaum
Member
- Location
- Indiana
- Occupation
- Electrical Engineer
I am working on an upgrade to a waste water treatment plant. The new equipment will require increased service from 400A to 800A (480/277 3ph 4W). There is currently a service entrance rated 400A Automatic Transfer Switch and a 150kW generator along with a 150KVA transformer for existing service. All of the power is brought into the existing ATS cabinet which has a lower gutter area for a pull box (cabinet 72" tall, bottom space is approx 27" tall, 32" wide, and 22in deep - there are four 3" conduit entries in the floor of the cabinet from below grade). Current wiring is 500 kcmil from the transformer and 2 x 3/0 from the generator. There is an additional spare conduit for both the generator and the transformer wiring that could accommodate new 500 kcmil and new 500kcmil or 2 x 3/0 for a new generator. I want to pull the new wiring into the old ATS cabinet and set a NEW service entrance rated 400A transfer switch net to the old ATS. Then, I would pull the new wiring to the new ATS beside the old one, thereby having tow 400A main service breakers in side-by-side ATSs to power the facility. Am I allowed - per the code - to pull the new additional wires originating from the transformer and generator from the old ATS cabinet to the new one next to it? I am in Indiana FWIW - 2008 NEC. Thanks for any feedback!