increasing conductor size

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: increasing conductor size

Chas, yes you can. What is the whole question about? Is there a VD concern?

The OCPD can not be larger than the smallest conductor ampacity for the application.

Roger
 

chas

Member
Re: increasing conductor size

Thanks, Is there a section in the code book I should read that relates to this ?
 

chas

Member
Re: increasing conductor size

Roger, The inspector said that I could not. The ocpd is rated 15 amps.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: increasing conductor size

It is more like there is not a code preventing this.

Roger posted the important issue that the OCPD (breaker/fuse) is sized to the smallest conductor in the circuit.

It is common to increase the wire size for voltage drop again as Roger mentioned.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: increasing conductor size

Originally posted by chas:
The inspector said that I could not. The ocpd is rated 15 amps.
Well the inspector is wrong (sorry Charlie) I wonder how this inspector would handle the typical site pole wiring.

We often use 6AWG 4AWG 3AWG for site poles for voltage drop reasons, would he expect us to us 60, 70, 100 amp breakers, most times we use 20 amp breakers for this.

[ September 26, 2003, 06:47 PM: Message edited by: iwire ]
 

tonyi

Senior Member
Re: increasing conductor size

The inspector is a boob. People have to increase wire size all the time to compensate for voltage drop over distance and derating issues. Your breaker will stay at 15A though. I've run a lot of #10 on 15A branches to compensate for VD and high attic temps.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: increasing conductor size

Chas, we would need to follow Bob's lead and in a diplomatic way ask the inspector to cite an article and section to back his remark.

There are instances and articles that would seem to go against the grain when it comes to conductor size and OCPD, so we could go on forever here. (430 & 440 for quick mention)

It is his responsibility to tell you in formal explanation what is in violation before you could know how to defend yourself.

Roger

P.S. back to where I said we could go on forever. It's true and can be frightening. :D

[ September 26, 2003, 07:03 PM: Message edited by: roger ]
 

chas

Member
Re: increasing conductor size

iwire, I don't know. the whole thing started with a simple 3-way, switch and a need for an additional switch for another entry door 3 feet away, inspectors quote,"all entry doors must have a switch for the exterior lights" so I created a 3-way,4way,3way situation using what I had on the truck (12-3)
 
G

Guest

Guest
Re: increasing conductor size

For space reasons I never carried #14 on my service truck. Didn't carry solid wire either. THHN or NM-B it was #12 and up.

Never got gigged for using #12 in place of or to add on to #14 circuits.

For bare solid copper it was mostly #8 and #4. Never got gigged for using a #4 bare instead of at #6. I just didn't have room to carry spools of every possible combination. Even so my service truck was loaded to the gills.

[Added by edit: Is this multi-family? Does the exterior light serve more than one door? What is the setup here? You raised an interesting side issue above].

[ September 26, 2003, 07:11 PM: Message edited by: awwt ]
 

chas

Member
Re: increasing conductor size

Thanks Guys,
I believe this inspector may be green.
(210.70 front door and back door) I suppose I will use diplomacy and ask If He wants me to change it and Why .
I appreciate every ones help on this matter.
chas
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: increasing conductor size

Hey Chas, welcome to the forum, and don't be a stranger.

Roger
 
Re: increasing conductor size

i will like to add one more thing to make it clear about conducter sizes .. now before you guys and ladies start barking at my ear ( sorry iam deaf anyway) .... now just image a water hose for a second ,, start at water source like small hose for X feet then swtich to larger hose for X feet then switch back to smaller hose the flowage will be the same .


here is the other good example i learn it longtime ago ( with engines stuff )

the rules for chains for strength is the alway the smallest link of whole length ..
ie. 1/4 inch link with 3/4 link and 1/4 inch link. now the strengh is always be 1/4 link never 3/4 link.

i hope i explain it ok if feel not right let me know

merci marc


P.S the same with tempture on conductes too ..
 

noxx

Senior Member
Re: increasing conductor size

The ampacity of the conductors shall not be less than the rating of the overcurrent device. There is nothing to prevent you from running a 15amp circuit in #2 wire if you so chose, aside from expense. Nowhere in the code is it stated that all conductors on a circuit be the same size, merely that the OCPD shall protect the smallest conductor, with exceptions for fixture taps, so on..

I've run plenty of #6 wire on a 20amp circuit for pumps and other rural equipment to comp for VD...anyway, your inspector is a boob.
 

pierre

Senior Member
Re: increasing conductor size

Chas
Refer to 210.19(A)FPN. No.4
This is not mandatory language, but guidance to say you may need to increase the size of the conductor to work with the voltage drop in the circuit.

As far as the NEC is concerned with switch location, in most situations it is not. The building codes do have requirements for switch locations and he may have been citing those. Ask him for a code reference, he is required with a redtag to cite a section.
I say don't give up, this will help you in the future and all who follow you.

Pierre
 

charlie

Senior Member
Location
Indianapolis
Re: increasing conductor size

Do not loose sight of the fact that the Code is a permissive document. In other words if it doesn't say you can't, then you can.

Sometimes the inspector is mistaken but he is never wrong. Remember the following rules:
1 The inspector is always right

2 If the inspector is found to be wrong, rule number 1 applies :D
 