Am I on track here.
I have a existing building that is putting on an addition. My existing service is 200 amp 120/240 three phase. With historical data showing 25KW of load.
NEC2017 220.87 25Kw X 125%=31.25 KW amp
31250/240=130.20 AmpsX1.73=225.26 amps
Load calculation for new loads is 29KW all single phase loads.
29000/240=120.8 amps
225.26+120.8=346Amps would be my new service size?