Paul the BIG Finn
Member
- Location
- Ashburn, VA
Our client increased the electrical service to his light industrial building from 800A, 120/208V, 3 phase 4 wire to 1,600A to power additional equipment. He installed a 1,600 switchboard and back feed the existing 800A panelboard from the switchboard with an 800A circuit breaker. My company was brought in to perform an arc flash analysis and provide warning labels. We contacted the power company and found the available fault current at the dedicated pad mounted transformer was just under 50 kA. The new switchboard is rated 65 kAIC, but the circuit breakers in the original 800A panelboard are rated 30 kAIC.
The circuit breaker in the switchboard supplying the existing service is rated 65kAIC, but is not current limiting.
I have found a current limiting fuse we could install in the feeder to the 800A panelboard, but the client would prefer a current limiting circuit breaker. Is there another solution short of replacing the panelboard? Will a current limiting fuse or circuit breaker satisfy the NEC?
I appreciate your opinions and experience.
The circuit breaker in the switchboard supplying the existing service is rated 65kAIC, but is not current limiting.
I have found a current limiting fuse we could install in the feeder to the 800A panelboard, but the client would prefer a current limiting circuit breaker. Is there another solution short of replacing the panelboard? Will a current limiting fuse or circuit breaker satisfy the NEC?
I appreciate your opinions and experience.