Hello, I'm new to the site....
I'm dealing w/ incremental voltage drops on a troubled pre-existing subpanel (inside the same building) w/ 208/120 single phase fed w/ a 50A 2-pole breaker #8 3-wire THHN over 600'......
The panel circuit's w/ drop every minute or so from 120V to 105V, driving the UPS crazy.
I know the 3-wire set-up is a problem, as is the #8 on the 50A circuit.....this is coming out.
I have the ability to go 480V 3-phase on the feed (same distance) a set a small transformer......
I just want the finished product to provide a stable system for the office sub-panel.
Any sense that can be made of this post & problem is appreciated.
Thanks!