Struggling to find appropriate section for adding indicating lights to general purpose enclosure in CID2 location. Lights would be only thing in/on enclosure except for splicing. Any help?

Not sure that panel indicating light is considered luminaire and would be following 501.130(B).
Or perhaps one of the sections in 501.105(B)... but which one? 501.105(B)(4)?
Or maybe there's another section I missed that is clearly made for this type device.

Thanks in advance
 
That is a good questions as none of the code sections appear to apply specifically to pilot lights.
I'd normally pick a light that is listed for Div 2 (for instance AB 800T series or similar, other than the push-to-test style) and put in general purpose enclosure.
 