I have a situation with a local building department who is mandating a rule I believe to be incorrect and borders on a code violation, in my opinion.
Individually mounted electric service metering has a short circuit rating as given by the manufacturer based on their testing criteria and is usually 10,000amperes. UL has not provided to the manufacturer a testing method to determine the withstand rating of metering as with cricuit breakers and other power distribution equipment.
Seimens places a label on their meter that says in part; "when used in conjunction with clas J and T fuses may be connected on a system with a fault current in excess of 10,000amps. THe word in question is "conjunction". The building department is interpreting that to mean any where in the circuit. load side or line side. Since the utility does not allow the fuses on the line side the building department is demanding we put class J and T fuses on the load side in accordance with the metering label.
My argument is this.
Service metering now falls under NEC rules. Under NEC rules any unit of equipment installed in the distribution system must be able to withstand or interrupt the available fault current safely. To protect the equipment and personnel, the current limiter or circuit protective must be up stream or on the line side of the equipment being protected. The building department is mandating that we place a fused switch with class J and T fuses down stream of the meter to satisfy the label were it reads "in conjunction with". Has any one thought about this or had similar problems? We have a single 400A service with 86,000amps available at the utility transformer and about 36,000amps at the meter. The utility company will not allow a fuse between the meter and utility connection. How would you properly protect the meter against excessive fault currents under NEC rules? Thank you
Individually mounted electric service metering has a short circuit rating as given by the manufacturer based on their testing criteria and is usually 10,000amperes. UL has not provided to the manufacturer a testing method to determine the withstand rating of metering as with cricuit breakers and other power distribution equipment.
Seimens places a label on their meter that says in part; "when used in conjunction with clas J and T fuses may be connected on a system with a fault current in excess of 10,000amps. THe word in question is "conjunction". The building department is interpreting that to mean any where in the circuit. load side or line side. Since the utility does not allow the fuses on the line side the building department is demanding we put class J and T fuses on the load side in accordance with the metering label.
My argument is this.
Service metering now falls under NEC rules. Under NEC rules any unit of equipment installed in the distribution system must be able to withstand or interrupt the available fault current safely. To protect the equipment and personnel, the current limiter or circuit protective must be up stream or on the line side of the equipment being protected. The building department is mandating that we place a fused switch with class J and T fuses down stream of the meter to satisfy the label were it reads "in conjunction with". Has any one thought about this or had similar problems? We have a single 400A service with 86,000amps available at the utility transformer and about 36,000amps at the meter. The utility company will not allow a fuse between the meter and utility connection. How would you properly protect the meter against excessive fault currents under NEC rules? Thank you