I have been down this road many times. Made a mistake or two along the way. The best design we have come up with for powered louvers is this: Install power-to-close spring-to-open louver motors. Connect them to a normal power circuit that is NOT powered by the generator. This way when utility power is lost, the louvers will open prior to generator start-up and the louvers will not be damaged by engine radiator fan pressure. The motors on these louvers are designed to withstand locked rotor current continuously. So they spend their entire lives in a locked rotor state with power flowing through them. Not a problem - these are very small motors that consume low current when locked. When power to the motor is lost, the springs will spin the motors backwards opening the louvers. On our first big generator job (600KW Diesel Cummins Indoor at a municipal water pumping station) the engineer had designed the motors to power open, spring close and he put them on a normal power circuit. At first start-up of the generator, the louvers got sucked into the radiator and destroyed them. As soon as they were replaced, the engineer wanted us to reconnect power to an emergency circuit. Our generator tech realized this would not work because the louvers were destroyed before emergency power was available. So he had us do what he called a standard arrangement of spring-to-open, power-to-close as I have described above, and we have had no problems since. Only other requirement is that a relay must be put in the circuit to kill power to the louvers while the engine is running so that the louvers will not close when utility power returns. This relay also opens the louvers when the engine is tested or run manually for any reason. We have had no problems with this arrangement at any of our installations! Good luck