2-93 Log #2751 NEC-P02
(210-8(B)(3) Exception (New) )
Recommendation:
Add Exception to read:
Exception: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).
Substantiation:
There is often great concern about financial losses on perishable items that may result from 'False-Tripping' of GFCIs used on circuits supplying Refrigeration Equipment. Receptacles behind refrigerators in dwelling units are not required to have GFCI protection and there seems to be some awareness that incompatibility may exist in 525.23(B) where "Receptacles supplying items, such as cooking and refrigeration equipment, that are incompatible with ground-fault circuit-interrupter devices shall not be required to have ground-fault circuit-interrupter protection." Why shouldn't the same options exist for these appliances in 'Other than Dwelling Unit' Kitchens?
Panel Meeting Action: Reject
Panel Statement:
See the panel action and statement on proposals 2-40 (Log #1141) and 2-76 (Log #128).