Indoor hottub disconnect

Status
Not open for further replies.

lpg

Member
Art. 680.41 says the emergency disconnect is not required for spas and hottubs installed at single family dwellings. Does this delete the requirement for a motor disconnect located within sight of the motor (430.102B)?(A seperate disconnect switch?) ? Does the pump switch on the hottub itself qualify for the motor disconnecting means? I have got a few different interpretations of these questions . Got any chatter to share?
 

speedypetey

Senior Member
Re: Indoor hottub disconnect

OK, I'll start.
IMO, no, it does not delete the disconnecting means for a motor. It just doesn't have to be within 5'. The switch on the tub is only a control and does not serve the same function as 430.102(A).
 

electricman2

Senior Member
Location
North Carolina
Occupation
Retired Electrical Contractor
Re: Indoor hottub disconnect

Even though the emergency disconnect is not required, 680.12 requires a maintenance disconnect. No distance requirement, just that it be accessible and within sight.
 