i have a question on bonding a spa, i have looked all thru section 680
my question if a steel frame spa with a liner indoors, does it need a copper grid in the floor
thanks as always
 
680.43 exception 2, in the 2011 NEC would exempt the spa from equipotential bonding if the tub is self contained and above the finished floor.
 