Re: Indoor therapeutic pool
Originally posted by augie47:
680.60 says parts I and IV of 680 will apply to pools and tubs for therapeutic use
..... Part IV is "labeld spas and hot tubs".. If the item in question is a therapeutic POOL, must it comply with all the items listed in part IV ?
(is IV only for spas and hot tubs?)
2005
VI. Pools and Tubs for Therapeutic Use
680.60 General.
The provisions of Part I and Part VI of this article shall apply to pools and tubs for therapeutic use in health care facilities, gymnasiums, athletic training rooms, and similar areas. Portable therapeutic appliances shall comply with Parts II and III of Article 422.
FPN: See 517.2 for definition of health care facilities.
680.61 Permanently Installed Therapeutic Pools.
Therapeutic pools that are constructed in the ground, on the ground, or in a building in such a manner that the pool cannot be readily disassembled shall comply with Parts I and II of this article.
Exception: The limitations of 680.22(B)(1) through (B)(4) shall not apply where all luminaires (lighting fixtures) are of the totally enclosed type.
2002
680.60 General.
FPN:See 517.2 for definition of health care facilities.
Where are you picking up part IV?