IMO, 422 is the correct Article but I would think the motor would be over 1/8HP and 422.31(c) would, apply and a disconnect would be needed.
Are you asking about a mini split or a standard heat pump system. If the latter then I believe you need a disconnect. Mant systems have heat strips in them for backup heat but that depends where you are from.
If it doesn't have a hermetic compressor it isn't covered by 440, it tells us this in 440.1I agree with you on 440.14.
There has been some debate as to the applicable Article for the air handler.
I was taught Art 422 but I can't see where it's carved in stone.
What about 430.112, which covers a single disconnecting means "where a number of motors drive several parts of a single machine"?
Cheers, Wayne
If it doesn't have a hermetic compressor it isn't covered by 440, it tells us this in 440.1
Air handler only is covered in art 422. Somewhere in there it tells us the branch circuit device can be the disconnecting means if no more then 300VA or 1/8 hp.Over those values typically requires a disconnect within site of the unit.
If it has electric heat we need to go to 424.
How about 440.8? It says "An air-conditioning or refrigerating system shall be considered to be a single machine under the provisions of 430.87, Exception, and 430.112, Exception.But I can not look at the air conditioner or the indoor fan as a motor only even though it is mostly a motor load. I see it as an appliance 422 or an A/C unit 440.
I think that would only apply to a situation where multiple motors (or even other loads within that machine) are all disconnected by the same branch circuit device. A typical "mini split" may fit in this description, but the typical central air unit is two separate units supplied by two separate branch circuits, though they do work together as one system.How about 440.8? It says "An air-conditioning or refrigerating system shall be considered to be a single machine under the provisions of 430.87, Exception, and 430.112, Exception.
The motors shall be permitted to be located remotely from each other."
Cheers, Wayne
If it doesn't have a hermetic compressor it isn't covered by 440, it tells us this in 440.1
Traditional North American marketed air handlers you likely won't find with that small of a motor.IMO, the air handler is a motor and falls under 430. I have never seen an air handler on a ducted system that did not require a disconnect. No way is the motor is not more than 1/8 hp.
so either way 422, 424 or 430 will still require a disconnect
But you can work on the indoor unit as a separate appliance and it is an independent unit than the condenser.It is really no different than a gas furnace
Almost always the other way, especially traditional North American marketed units. Indoor unit sends a control signal to the outdoor unit to tell it to run.But you can work on the indoor unit as a separate appliance and it is an independent unit than the condenser.
The indoor unit of a heat pump will turn off when the outdoor unit's disconnect is turned off. One can not service/troubleshoot the indoor unit without the outdoor power being on. So it is part of an outdoor unit. Also, 422 allows the disconnect to be off site as long as it is lockable in the off position.
So if 422 allows the off site lockable disconnect (even for more than 1/8 HP ) does 440 have the authority to overrule it?
What did I say that contradicts your statement?Almost always the other way, especially traditional North American marketed units. Indoor unit sends a control signal to the outdoor unit to tell it to run.
But you can work on the indoor unit as a separate appliance and it is an independent unit than the condenser.
The indoor unit of a heat pump will turn off when the outdoor unit's disconnect is turned off. One can not service/troubleshoot the indoor unit without the outdoor power being on. So it is part of an outdoor unit. Also, 422 allows the disconnect to be off site as long as it is lockable in the off position.
So if 422 allows the off site lockable disconnect (even for more than 1/8 HP ) does 440 have the authority to overrule it?
You said "The indoor unit of a heat pump will turn off when the outdoor unit's disconnect is turned off." Not true for the majority of the units. You will still have indoor unit running and will still have 24 volts to the contactor coil of the outdoor unit because the control power comes from the indoor unit. The compressor will stop and you won't get any heat/cooling from the refrigerant but the indoor blower and any back up heat still function.What did I say that contradicts your statement?