Hello guys and gals
I have a 480v actuator that has 120v inputs to open and close. The 120v power is supplied by a transformer in the actuator. The inputs are controlled by triac output card on an old Gould plc at least a hundred feet away in a control room.
I am picking up some voltages I dont really understand. When the 120 volt wires are hooked to the supply and inputs, without outputs on, I am reading about 108v to "neutral" on the open and close wires coming back from the output. But the actuator does not recognize this voltage because it does not try to move.
When the output turns on, the open and close wires coming back from the output turn to 120v and the actuator opens and closes correctly.
When I unhook the 120v supply and inputs on the actuator I read about 65v to ground.
I am using a fluke dmm for measurements.
Is this induced voltage? The control conductors are ran with the power conductors but doesnt there have to be current on the power conductors to induce voltage in the cotrol conductors?
I shorted these wires to ground to see if an overcurrent device would trip. Nothing.
If it was capacitive coupling wouldnt it have went away when I shorted it out.
I wouldnt worry about it much if the actuator sometimes didnt open when the closed input was energized. The manufactor says these voltages are what the problem is. The actuator is brand new.
Sorry for being so long, but I can usually get great help from you guys.
Appreciate all responses.
I have a 480v actuator that has 120v inputs to open and close. The 120v power is supplied by a transformer in the actuator. The inputs are controlled by triac output card on an old Gould plc at least a hundred feet away in a control room.
I am picking up some voltages I dont really understand. When the 120 volt wires are hooked to the supply and inputs, without outputs on, I am reading about 108v to "neutral" on the open and close wires coming back from the output. But the actuator does not recognize this voltage because it does not try to move.
When the output turns on, the open and close wires coming back from the output turn to 120v and the actuator opens and closes correctly.
When I unhook the 120v supply and inputs on the actuator I read about 65v to ground.
I am using a fluke dmm for measurements.
Is this induced voltage? The control conductors are ran with the power conductors but doesnt there have to be current on the power conductors to induce voltage in the cotrol conductors?
I shorted these wires to ground to see if an overcurrent device would trip. Nothing.
If it was capacitive coupling wouldnt it have went away when I shorted it out.
I wouldnt worry about it much if the actuator sometimes didnt open when the closed input was energized. The manufactor says these voltages are what the problem is. The actuator is brand new.
Sorry for being so long, but I can usually get great help from you guys.