marissa2
Senior Member
- Location
- Connecticut
The code tells us that under normal conditions that you cannot run a single conductor in a metal raceway because of eddy currents being induced in the metal raceway will cause it to become hot. I can live with this requirement and I understand why it can happen with only one conductor, but what I would like to know is what does the current have to be to generate enough of a field to heat the raceway. We tried this today with a 10 foot length of ? in EMT with a single #12 conductor with 11 amps of current which ran for several hours and didn?t heat the pipe at all. The EMT was grounded at one end. I have never tryed this before but we had some time today to set it up and let it run.
Lou
Lou