With the historic heat wave in the Pacific NW, I plugged in a portable condensing AC unit in my home office . This panel-protected AFCI circuit also serves a switch in another room, which is in a double gang box with a switch that is on a panel-protected GFCI circuit for that room. The GFCI panel breaker has been tripping , coincidentally beginning after I began running the floor AC unit in the office AFCI circuit.
These circuits do not share a neutral - there are no shared neutrals in the house (I know, because I wired this house myself).
The GFCI breakers and AFCI breakers (both Siemens) are on the same bus on the panel, but are far apart. I have not yet opened the panel to see if their neutrals are on the same bar.
Therefore, I suspect that inductive kickback from the AC unit is the cause of the GFCI trip on the othe circuit.
I really don't want to replace the GFCI panel breaker unless I can verify it's defective, and I'd prefer not to replace it with a plain panel breaker and and add a GFCI outlet.
So, I'd like to find a way to shield the GFCI circuit from any effects of the adjacent circuit.
Is there a code-compliant way I could apply a grounded shield to protect one switch from the other in the double-gang box? Or is my best option to break the switches out into two shielded single-gang boxes ?
These circuits do not share a neutral - there are no shared neutrals in the house (I know, because I wired this house myself).
The GFCI breakers and AFCI breakers (both Siemens) are on the same bus on the panel, but are far apart. I have not yet opened the panel to see if their neutrals are on the same bar.
Therefore, I suspect that inductive kickback from the AC unit is the cause of the GFCI trip on the othe circuit.
I really don't want to replace the GFCI panel breaker unless I can verify it's defective, and I'd prefer not to replace it with a plain panel breaker and and add a GFCI outlet.
So, I'd like to find a way to shield the GFCI circuit from any effects of the adjacent circuit.
Is there a code-compliant way I could apply a grounded shield to protect one switch from the other in the double-gang box? Or is my best option to break the switches out into two shielded single-gang boxes ?