J J.Enright New member Location Phoenix,AZ., USA Jul 6, 2011 #1 Would a standard Eaton/Powerware 160 KVA UPS with Factory UL Label be required to have a KAIC rating listed per Art.409- Industrial Control Panels.
Would a standard Eaton/Powerware 160 KVA UPS with Factory UL Label be required to have a KAIC rating listed per Art.409- Industrial Control Panels.
petersonra Senior Member Location Northern illinois Occupation engineer Jul 8, 2011 #2 J.Enright said: Would a standard Eaton/Powerware 160 KVA UPS with Factory UL Label be required to have a KAIC rating listed per Art.409- Industrial Control Panels. Click to expand... I believe it is not an industrial control panel, so IMO no.
J.Enright said: Would a standard Eaton/Powerware 160 KVA UPS with Factory UL Label be required to have a KAIC rating listed per Art.409- Industrial Control Panels. Click to expand... I believe it is not an industrial control panel, so IMO no.
Jraef Moderator, OTD Staff member Location San Francisco Bay Area, CA, USA Occupation Electrical Engineer Jul 8, 2011 #3 In fact as a UPS it specifically CANNOT be an Industrial Control Panel, at least as far as UL is concerned.
In fact as a UPS it specifically CANNOT be an Industrial Control Panel, at least as far as UL is concerned.