Johnshealey
A suggestion was made to relocate an industrial control panel from roughly eye-level to be mounted to an overhead moving crane. The purpose of the change was to save money on expensive flexible servo motor cables and to simplify installation. The overhead option would require a ladder to access it.
The industrial controls included servo motor drives, with a maximum of 480 VAC inputs. The control panel design includes an interlocked disconnect switch for power and is operable with the enclosure door open or closed (NFPA 79 handle). The controls are all "dead front" and so might be considered to be not "exposed live parts".
Some concerns I have with the proposal were (from NFPA 79):
11.1.1 "All control equipment shall be located and mounted so as to facilitate ... accessibility and maintenance of the equipment."
11.5.1 Working Space: Condition 1: 3 feet "in the direction of access to live parts".
So, the accessibility is certainly reduced. All components are "finger safe", so my guess is that we can get away with this. Any comments?