• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Industrial control panel feeder

jeff motta

Member
Location
nj
Occupation
electrician
I am looking for some input, we are going to provide power for an industrial mixer, the nameplate rating is 38kw @ 208v 3 phase, it has two 15kw immersion heaters and 3 motors, 9a amps being the largest of the 3 the other two are 5 amps each, so far, I have come up with 131A, I would run 1/0 thhn for the feeder to the control cabinet but I feel like I have missed a step, I have not figured in the duty cycle of the heaters or motors yet, I am waiting on the client to provide info on how this mixer operates. Thanks for your time
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is piece of equipment with a nameplate rating. It is not a continuous load so why the 125%?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
This is piece of equipment with a nameplate rating. It is not a continuous load so why the 125%?
I think it is only 25% extra for the largest motor. I don't know why the OP used 125% of the whole thing. Not that it matters any. He can oversize the feeder if he wants to. I would have gone with 107 Amps minimum. But 1/0 will work fine as will a 150 amp cb for the feeder. Cost difference is probably not that much.
 

jeff motta

Member
Location
nj
Occupation
electrician
I don't think it matters if it is continuous or not for the purposes of determine the feeder ampacity.

By the way, it would be wise to look up the definition of continuous in NEC article 100.
Bob, thanks I didn't look at it this way
 
Top