industrial controls min height

Status
Not open for further replies.

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: industrial controls min height

Not in the NEC as such. There is a max height for a disconnect of 6 ft 7 in to operating handle, a motor disconnect has to be readily accessbile or just accessible, depending on Sec 430.102 use.