Industrial Electrical Designs Including GFCI

Status
Not open for further replies.

mrdavis

Member
Location
78749
Occupation
Engineer
Do indoor L5-20 and L6-30 plugs require GFCI when they are installed for a specific piece of equipment such as a pump, chiller, UPS, ETC? The code references i can find seem a bit circular

Thanks
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
210.8 covers gfci protection….. if it’s not a dwelling, 210.8(B)


Sent from my iPhone using Tapatalk
 

mrdavis

Member
Location
78749
Occupation
Engineer
210.8 covers gfci protection….. if it’s not a dwelling, 210.8(B)


Sent from my iPhone using Tapatalk
Thank you, but I have already reviewed that text multiple times and I still haven’t found any clear direction from it. Thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thank you, but I have already reviewed that text multiple times and I still haven’t found any clear direction from it. Thanks
In general, the code rules for GFCI protection are based on the location of the receptacle and not what equipment is being supplied. However there are specific equipment GFCI requirements in 422.5.
 