industrial electrician

Status
Not open for further replies.

AE-29

Member
Location
Florida
A master electrician i'm working with told me 240v extention cords are not allowed for use basically over 15 feet in an industrial environment. Is there a code for this or is it sort of just a general trade understanding. I know manufac. make 240v cords 100ft.
 

Hendrix

Senior Member
Location
New England
A master electrician i'm working with told me 240v extention cords are not allowed for use basically over 15 feet in an industrial environment. Is there a code for this or is it sort of just a general trade understanding. I know manufac. make 240v cords 100ft.
Must be the "enviornment" .
 
Last edited:

AE-29

Member
Location
Florida
Must be the "enviornment" .
Yeah the environment, outdoors and straight 240v cord. Other than protecting the cord from damage and contact I could not find anything specifically relating to the voltage of the cord in the code.

Thanks...
 

pfalcon

Senior Member
Location
Indiana
NFPA79 : 2007 : 13.1.6 Cord.
13.1.6.2 The use of cord shall be limited to individual exposed lengths of 15m (50 ft) or less.

Disclaimer:
NFPA79 is not specifically called out as required in any state of which I am aware.
 