I have a new construction scenario and some debate has ensued among old school electricians that I would like to run by folks. Apologies if terminology is not NEC standard.
SES is 480/3P secondary from the utility, with a main isolation breaker, attached to the SES is the branch feeder panel that supplies several MCPs (motor control panels). Brand new, state of the art stuff....
The building slab (200' x 100') is 1/2" rebar enforced and the rebar is tied via "J" connectors to the all steel building. In the building we have several large towers (12x8" ibeam). The building, the steel towers and large conveyors (8" steel channel frame) are all connected via welded bar stock that this thicker than A 250 requirements for bonding jumpers, etc.
Induction Motors and AC Drives in the plant are either bolted to the conveyor ends, or bolted to frames that are welded to the steel towers. Care was taken to remove paint from mounting structures that are bolted, but supplemental tack welds put in place to ensure a connectivity path. Motor conduit is rigid metallic, with exception of the last 2 feet or so to seal tight rigid flex, for ease of routing.
I am impressed on our bonding and grounding, in so far as a welder can ground off pretty much anywhere he wants and weld a great distances to his work. If there is such thing as zero reference everywhere, I probably have a good example of it. ;-)
We plan to do a more formal ground/bond testing on every motor, but preliminary tests show 000.0 ohm fluke readings from every motor case to the cat walk, which is also bonded. The latest debate considers 3 options... 1) the need to run any ground wire from the motor pecker head at all since everything is bonded 2) running a short green jumper (12-24") from the motor head to the steel beem mount which is already bonded to the tower/building/conveyor 3) taking another ground wire back to the transformer along with circuit conductors (via feeder MCPs). I am speaking figuratively speaking, not literally routing the ground wire.
Summary... The question under discussion is the need for running a ground wire to every motor because "we have always done it that way"? Ultimately we will be under MSHA for inspection, and I plan on running this by our local inspector before we start up in the next few weeks but until now it has been our own electricians under my mandate to follow the NEC.
Great Forum... Thanks for any input. I just purchased Mike's book on grounding and bonding, and I hope it helps solve our discussions also.
R,
Joez06
SES is 480/3P secondary from the utility, with a main isolation breaker, attached to the SES is the branch feeder panel that supplies several MCPs (motor control panels). Brand new, state of the art stuff....
The building slab (200' x 100') is 1/2" rebar enforced and the rebar is tied via "J" connectors to the all steel building. In the building we have several large towers (12x8" ibeam). The building, the steel towers and large conveyors (8" steel channel frame) are all connected via welded bar stock that this thicker than A 250 requirements for bonding jumpers, etc.
Induction Motors and AC Drives in the plant are either bolted to the conveyor ends, or bolted to frames that are welded to the steel towers. Care was taken to remove paint from mounting structures that are bolted, but supplemental tack welds put in place to ensure a connectivity path. Motor conduit is rigid metallic, with exception of the last 2 feet or so to seal tight rigid flex, for ease of routing.
I am impressed on our bonding and grounding, in so far as a welder can ground off pretty much anywhere he wants and weld a great distances to his work. If there is such thing as zero reference everywhere, I probably have a good example of it. ;-)
We plan to do a more formal ground/bond testing on every motor, but preliminary tests show 000.0 ohm fluke readings from every motor case to the cat walk, which is also bonded. The latest debate considers 3 options... 1) the need to run any ground wire from the motor pecker head at all since everything is bonded 2) running a short green jumper (12-24") from the motor head to the steel beem mount which is already bonded to the tower/building/conveyor 3) taking another ground wire back to the transformer along with circuit conductors (via feeder MCPs). I am speaking figuratively speaking, not literally routing the ground wire.
Summary... The question under discussion is the need for running a ground wire to every motor because "we have always done it that way"? Ultimately we will be under MSHA for inspection, and I plan on running this by our local inspector before we start up in the next few weeks but until now it has been our own electricians under my mandate to follow the NEC.
Great Forum... Thanks for any input. I just purchased Mike's book on grounding and bonding, and I hope it helps solve our discussions also.
R,
Joez06