Big Boy Stan
Member
- Location
- New Jersey
I am a bit confused and hoping for some advice on what grounding and bonding is required for an induction furnace we are installing. The system begins with a 6 phase 575V secondary transformer located outdoors of the plant. I have installed (12) 500MCM cables times 6 in cable tray from the transformer to the furnace power supply where it lands at a circuit breaker. The system is a completely ungrounded separately derived system and includes a ground detection monitor and alarm that will sound if the ground leakage exceeds 100mA. The NEC requires bonding between the equipment to handle any likely fault currents but based on this setup, I do not see how any significant fault current could develop. How do I size this? Do I need a bonding jumper from the power supply to the transformer sized at 12.5% of the (12) 500MCM conductors (Table 250.102(C)(1)? Considering the likely fault current however this seems very excessive. What scenario could lead to higher currents in the bonding jumper?
Thanks for any help or advice.