Is it permissable to use a plug and receptacle hook-up on 400W or 1000W High Intensity discharge 480V single phase lighting fixtures, fed through a remote contactor? The contactor will be fed with a 3 phase 480 volt delta power source from a busway with a high impedence ground. There will be about 54 lights fed off of the remote contactor. We are an Ohio manufacturing plant.
 

david

Senior Member
Location
Pennsylvania
Re: Industrial Lighting

410.30 Cord-Connected Lampholders and Luminaires (Fixtures).

C) Electric-Discharge Luminaires (Fixtures).

(1) A listed luminaire (fixture) or a listed assembly shall be permitted to be cord connected if the following conditions apply:

(1) The luminaire (fixture) is located directly below the outlet box or busway.
(2) The flexible cord meets all the following:
a. Is visible for its entire length outside the luminaire (fixture)
b. Is not subject to strain or physical damage
c. Is terminated in a grounding-type attachment plug cap or busway plug or has a luminaire (fixture) assembly with a strain relief and canopy
 

jbivens

Member
Re: Industrial Lighting

Thanks David, we are also wondering if each luminaire has to have its own seperate fuse protection, and what is the minimum cord size and rating?
 