Our equipment requires a 480V feed to a breaker panel which services the following:
1. Transformer loaded with both continuous and intermittent loads.
2. Intermittent motors.
3. Two HVAC systems (both considered continuous)
4. Power converter (continuous)
5. Heating coil.
I am calculating the total load of the equipment so the customer can provide an appropriately sized feed(fused). Should I do 100%*(intermittent load) + 125%*(continuous load) OR should I do 125% of the total load since it is a single piece of equipment in the customers eyes.
I guess I am trying to determine an FLA for the equipment along with the WSA for sizing the feed and fuse.
1. Transformer loaded with both continuous and intermittent loads.
2. Intermittent motors.
3. Two HVAC systems (both considered continuous)
4. Power converter (continuous)
5. Heating coil.
I am calculating the total load of the equipment so the customer can provide an appropriately sized feed(fused). Should I do 100%*(intermittent load) + 125%*(continuous load) OR should I do 125% of the total load since it is a single piece of equipment in the customers eyes.
I guess I am trying to determine an FLA for the equipment along with the WSA for sizing the feed and fuse.