Industrial Machinery - 670.4 (B)

raranari

Member
Location
Jupiter, FLorida
Occupation
Electrical Designer
We are designing this Industrial Facility. The main production line shop drawings call for 6 different point of connections around the line for powering different pieces of equipment that will be running at the same time, each one of them require a disconnect.

Per my interpretation of the 670.4 (B) all this 6 different pieces of equipment together are considered one individual unit and shall be provided with a single disconnecting mean so that in case of emergency the entire line could be disconnected at once.

I was thinking of providing either an EPO and shunt trips for each breaker or a fused disconnect and tap them with fused disconnect.

This is our first industrial project and i would like to get some feedback regarding this.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Cam any one piece of equipment be taken out of service or is it a production line where stopping one piece of equipment shits down the whole line ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The only place I have seen the single disconnect accepted is for a multi-motor assembly line where the entire line needs to shut down when any one section is having maintenance.
 