raranari
Member
- Location
- Jupiter, FLorida
- Occupation
- Electrical Designer
We are designing this Industrial Facility. The main production line shop drawings call for 6 different point of connections around the line for powering different pieces of equipment that will be running at the same time, each one of them require a disconnect.
Per my interpretation of the 670.4 (B) all this 6 different pieces of equipment together are considered one individual unit and shall be provided with a single disconnecting mean so that in case of emergency the entire line could be disconnected at once.
I was thinking of providing either an EPO and shunt trips for each breaker or a fused disconnect and tap them with fused disconnect.
This is our first industrial project and i would like to get some feedback regarding this.
Per my interpretation of the 670.4 (B) all this 6 different pieces of equipment together are considered one individual unit and shall be provided with a single disconnecting mean so that in case of emergency the entire line could be disconnected at once.
I was thinking of providing either an EPO and shunt trips for each breaker or a fused disconnect and tap them with fused disconnect.
This is our first industrial project and i would like to get some feedback regarding this.