Here is a question. I have a piece of equipment that has a manufacturer installed disconnect switch mounted on a control cabinet. The control cabinet feeds various motors and belts for manufacturing parts. The feeder for this control cabinet is terminated to a terminal block located inside the cabinet, and from there it goes to the disconnect switch. When the switch is opened, it kills power to the cabinet, but the feeders are still energized at the terminal block. The feed comes from a panel approximately 70 feet away. An individual says that it is illegal to terminate these to a terminal block and then go to the switch. I looked at 430.102 and it say that I am to provide a means of disconnect to the equipment, with in sight, and it shall disconnect the control cabinet. I also refenced Art. 670 but found that to be informative only to certain criteria. The facility has a lock out /tag out procedure which it provides at each machine throughout the plant to lock out the feeder if it is necessary. My question is do I need to provide a disconnect for the feeder at the machine before it goes into the cabinet or am I in compliance with 430.102 as well as manufacturer specs?