I'm installing ACTIVE HARMONIC FILTERS to swbd's at an industrial site. The secondary of the xfmr is connected to swbd by 4000A bus to a 4000A main breaker. Then there are four 1200 breakers feeing MCC's.
The plant engineer wants me to tap off the 4000A bus, in the transition section upstream of the swbd main, to a 125A breaker, with less than 25' of #2 conductors. The City electrical inspector said that's ok. Citing sect, 240.21 C 3. His reasoning is Since the xfmr is not supplying any amps to the ACTIVE HARMONIC FILTER, the Filter is supplying up to 100A to the swbd, all the conductors should be sized to the filter.
This doesn't seem right to me. For my own peace of mind would like confirm this is ok. Don't want anyone getting hurt, and don't want an illegal installation.
Thanks for any info
The plant engineer wants me to tap off the 4000A bus, in the transition section upstream of the swbd main, to a 125A breaker, with less than 25' of #2 conductors. The City electrical inspector said that's ok. Citing sect, 240.21 C 3. His reasoning is Since the xfmr is not supplying any amps to the ACTIVE HARMONIC FILTER, the Filter is supplying up to 100A to the swbd, all the conductors should be sized to the filter.