I am going to add 2 new pump motors to an existing service. I have never done a load calculation before. Can someone give me some code references? All I really seen is codes related to dwelling units.
Do you have even a WAG of what kind of kVA is existing and what kind of kVA will be added?
What I am getting at is if you have a large service already and are adding only a 10 hp load you probably get away with it even if the existing is being pushed to it's limits. But if you are adding a 100 hp motor that can make a big difference.
I agree
Calculations may not be required
determine the size of the existing service
xfmr
service cond
dist panel that new load will be added to
as built drawings
fairly easy to do
then take some current readings with equipment in its peak power mode
the difference is spare capacity